An Aqua Logic 1/3 HP needs 600-1200 GPH. At 150 GPH your not taking enough heat out of the refrigerant. Gas pressures and temps inside the chiller are out of wack and the compressor is running too hot, leading to premature compressor failure. The Aqua Logic is 3/4" but you cant run to the other end of the house like that. A gallon in six seconds is too fast for 3/4". Let all the head come from the chiller, use bigger pipe too and from.